We have a fixed speed, 3 phase, 480 volt motor for a water pump that is getting a VFD installed on it. Can we use existing conductors?
430.6(C)
You may have to change the wire on the input side of the drive, but from drive to motor should be ok, if it was properly sized before. Don't forget the load reactor per installation instructions.
We have a fixed speed, 3 phase, 480 volt motor for a water pump that is getting a VFD installed on it. Can we use existing conductors?
I know that in USA it is quite common to use individual conductors in conduit and that isn't generally recommended for variable speed drives.
In most part thats because Europe seems to encourage the use of cables over conduit and shielded cable keeps the radiated RF level lower. Same reason why stuff going to EU has all those miserable ferrite beads on everything.The input current will most likely be lower than before but I don't know what the code requires.
The other thing consider is the type of cable between the drive and the motor.
Normally we use three or four core armoured cable which is typical for here (UK) but I know that in USA it is quite common to use individual conductors in conduit and that isn't generally recommended for variable speed drives.
Possibly. I'll dig up some images from manuals when I not quite so tired.Why do you say that, have I missed that reading the 'books' that come with them?
We have a fixed speed, 3 phase, 480 volt motor for a water pump that is getting a VFD installed on it. Can we use existing conductors?