Grounding multiple disconnects

Status
Not open for further replies.

ivsenroute

Senior Member
Location
Florida
What method do you use when installing the grounding electrode system where the disconnects are grouped together?

Do you run the GEC from the closest panel to the electrode then using the internal terminal bars of the disconnects connect the other ones the the first one like a daisy chain?

Do you run the GEC from the farthest disconnect then crimp the other grounds coming from the other panels to the GEC like it is a trunk line (tap method)?

Install a nice thick 1/4 grounding plate (busbar) at a central location?

Another method?

What is popular in your area.
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I prefer this method with a couple of split bolts for the taps:

250.66%20Taps.JPG
 

ivsenroute

Senior Member
Location
Florida
Are split bolts allowed for this type of connection? If the taps are still part of the GEC then split bolts would not be allowed.
 

ivsenroute

Senior Member
Location
Florida
I am asking this because there was a change from 2005 to 2008 in this section with the 2008 being more restrictive.

Are there split bolts that are listed as grounding and bonding equipment?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Taps to the GEC are permitted as long as the GEC remains unbroken. I would assume that split bolts are listed for connection of bonding jumpers to a GEC but I can't say for sure.

250.64(D) Service with Multiple Disconnecting Means Enclosures. Where a service consists of more than a single enclosure as permitted in 230.71(A), grounding electrode connections shall be made in accordance with (D)(1), (D)(2), or (D)(3).
(1) Grounding Electrode Conductor Taps. Where the service is installed as permitted by 230.40, Exception No. 2, a common grounding electrode conductor and grounding electrode conductor taps shall be installed. The common grounding electrode conductor shall be sized in accordance with 250.66, based on the sum of the circular mil area of the largest ungrounded service-entrance conductor(s). Where the service-entrance conductors connect directly to a service drop or service lateral, the common grounding electrode conductor shall be sized in accordance with Table 250.66, Note 1. A tap conductor shall extend to the inside of each service disconnecting means enclosure. The grounding electrode conductor taps shall be sized in accordance with 250.66 for the largest conductor serving the individual enclosure. The tap conductors shall be connected to the common grounding electrode conductor by exothermic welding or with connectors listed as grounding and bonding equipment in such a manner that the common grounding electrode conductor remains without a splice or joint.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Shortly after I noted that "listed for grounding" wording I contacted Burndy and they sent documentation on a number of their products that were "approved" including split bolts.
 

shortcircuit2

Senior Member
Location
South of Bawstin
In exibit 250.27 in post #3 the GEC doesn't connect to the Bus that the grounded service conductor lands...only the tap does. Wouldn't this be a violation of 250.24(A)(1)

shortcircuit2
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I am asking this because there was a change from 2005 to 2008 in this section with the 2008 being more restrictive.

Are there split bolts that are listed as grounding and bonding equipment?

When that Code change was enacted I contacted Burndy and received an e-mail showing all there split bolts were listed for grounding applications.
 