shermansfather
- Northeast Ohio
I have a job that involves providing 277/480 for future use to gravel boats. The boats will not be in place for some time, but the service needs to be installed now as the POCO is for a limited time providing the transformer free.
My parameters:
A: Load - Anywhere between 5kw and 100kw per disconnect (x2), maybe peaks of 200kw
B: Connections to disconnect made by ship's electrician, who I'm told keep rated cable, fuses and fuse reducers. I'm to leave fuses out of disconnect after my installation.
C: I'm installing 2 400 A Discos, but POCO is requiring 1600A capacity out of the vault and 1600A CT cabinet.
D: Everything is outdoors, no stucture anywhere
My questions:
A: Before the CT cabinet do I parallel the phases individually (like my drawing), the POCO is telling me to do it his way.
B. Do I bond the neutral to the EGC and electrodes at the CT cabinet or at each disconnect ? I left this off the drawing for now.
C. Would I need a main disconnect before the 2 400A discos (POCO says they usually want a disco before CT's above 800A, their engineer says he'll let it go)
D. Does anybody have any better ideas ?
My parameters:
My questions: