Filckering Lights and Sparks

Status
Not open for further replies.
A client called and said his home lights were flickering (more so when it rained). After witnessing the living room lights flicker, I pulled the cover to the service entrance panel and saw two of the breakers intermittently spark.

I replaced two of the breakers (badly pitted) and moved then to new unused post on the bus bar and applied Noalox? anti-Oxident compound.

Three day passed with no flickering lights but then it rained and his lights began to flicker, slightly.

The panel is a Challenger 125 amp lateral and the house is circa 1975 with CU wires.

A side from a complete R&R of the panel is here something easel that I should be doing?
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Is the main a large red horizontal body that plugs onto the two top bus stabs? If so, I bet the lower stab is burned.
 

480sparky

Senior Member
Location
Iowegia
....... and applied Noalox? anti-Oxident compound..........

Why?
HoltBlueDot.jpg
 
I used Noalox because of the North facing, shaded and damp area where the service is located.

Is there another product that would help contact and fight dampness?
 
Status
Not open for further replies.