PetrosA
 - Lancaster, Pennsylvania
I have to design and price a control panel for a customer. It seems like a pretty simple one, but a little above my comfort level (which I need to get out of
 ). So far I've been dealing with Welder Dude (the customer) and Motor Sales/Repair Dude (his supplier) - not a lot of help. I'm hoping someone here can help me out.
The equipment is a manure chopper with two motors - one 5 HP with a VFD to power a chopper and a 2 HP with starter for a feed mechanism. They want to be able to adjust the speed of the 5 HP to work with the 2 HP. The unit is a portable one, designed to be hauled on a trailer hitch and powered by a 3? generator.
Our original talks included a start/stop that would control both motors together but after discussing it with Welder Dude, we decided that there should also be e-stops on either side of the machine (it's approx. 15' tall x 15' long and 8' wide, so running around or under it in an emergency isn't a good idea).
So here's where I'm at with my limited knowledge of controls:
Hooking up the E-stops:
Option 1
I could have a NC contactor to react to two NO e-stops so that pressing either would open the contacts. After that would be a NO contact for the start/stop controls that would feed the VFD and starter. What worries me with this plan is that e-stop is dependent on there being power - IOW, if one guy hits an e-stop, and another unplugs power from the generator, then they plug it back in, there could be power sent to the motors for an instant until the e-stop shuts the NC contactor off again.
Option 2
Run the start control through both e-stops NC so that pressing either would shut the NO contactor. This would only require one contactor for everything and would ensure that the motors are mechanically off until the e-stop is reset.
Coordinating the two motors:
Next question is about the VFD together with the starter controlled motor - Does the VFD need time to ramp up to whatever speed they preset? This would possibly affect whether I need a time delay on the starter controlled motor so it's not feeding into the chopper too soon.
What's painfully apparent to me is my lack of knowledge in this area, especially about what's available. I haven't found any supply houses around here with knowledgeable staff on the subject, I can't get a hold of any catalogs, and from what I've seen online, it looks like there may be better ways to make this work than what I've come up with. Relays, starters with integrated timers/contacts, VFD with contacts, etc. These are the things I don't know about and it's frustrating.
Any criticisms and better ideas you have are welcome.
Option 1
Option 2