Electrical equipment.....
....such as circuit breakers, panelboards, receptacles, switches, terminal blocks, wire nuts, lugs etc. have "temperature ratings" that must be observed.
The termination provisions are based on the use of 60C ampacities for wire sizes #14-#1 , and 75C ampacities for wire sizes #1/0 and larger. If using wire sizes #14-#1 in equipment marked "75C only" or "60/75C" , it is intended that 75C wire may be used at its full ampacity.
If the equipment is not marked, it is 60 deg. C rated for 100 amps and less. Over 100 amps is 75C rated. If the equipment is rated higher, it would have to be marked to indicate the higher temperature.