Mike Holt, I attended your NEC Up Training at Grand Coulee Dam and know you are an authority on NEC and am requesting your reply to this.
Per NEC 680.21 (A)(4) One Family Dwellings. In the interior of dwelling units
or in the interior of accessory buildings associated with a dwelling, any of the wiring methods recognized in Chapter 3 of this code that comply with the provisions of this section shall be permitted.
I read this to mean that I can use romex in the accessory building that houses the circulation pump and heater, even if the accessory building is about 25' away from the house.
The inspector says I need conduit or type MC Cable.
Per NEC 680.21 (A)(4) One Family Dwellings. In the interior of dwelling units
or in the interior of accessory buildings associated with a dwelling, any of the wiring methods recognized in Chapter 3 of this code that comply with the provisions of this section shall be permitted.
I read this to mean that I can use romex in the accessory building that houses the circulation pump and heater, even if the accessory building is about 25' away from the house.
The inspector says I need conduit or type MC Cable.