Situation: A friend of mine is in the process of building a house. This project has been done in steps so the detached garage was built first. Therefore the service was brought into the garage with a 200amp supply and panel. Now he is preparing to build the house and asked me to size his Feeder conductors to the house. He wants to put a 200amp at the house as well.
Here is what I got: Per 408.36 he can size the OCPD in the garage panel at 200amps. Conductor size using table 310.15(B)(6) "conductor types and sizes for 120/240 volt 3-wire single phase dwelling services and feeders" says 2/0 copper for 200amp rating. 310.15(B)(6) points me in a round about way to 250.122 that I'm interpreting a size 6AWG for equipment grounding conductor and neutral size.
So in the long run 2-2/0 and 2-6awg to supply his house is this right? And of course keep egc and neutral seperate at house and planning on driving two ground rods to be safe. Thanks for your help!!
Here is what I got: Per 408.36 he can size the OCPD in the garage panel at 200amps. Conductor size using table 310.15(B)(6) "conductor types and sizes for 120/240 volt 3-wire single phase dwelling services and feeders" says 2/0 copper for 200amp rating. 310.15(B)(6) points me in a round about way to 250.122 that I'm interpreting a size 6AWG for equipment grounding conductor and neutral size.