Hameedulla-Ekhlas
- AFG
Greeting to all,
I have calculated shortcircuit calculation using digsilent powerfactory software. I found in all buses and terminals the maximium kA as well as MVA.
Since I sized breakers and buses based on nominal and maximium kA as well as buses.
I have problem in Cable size. I have sized cables based on nominal ampere ampacity as well as voltage drop.
Is there any specific table for cables to understand the maximium short circuit that a cable can withstand for a few cycle like breakers or busbars.
best regards
Hameedullah Ekhlas
Electrical Engineer
Kabul Afghanistan
best regards
Hameedullah Ekhlas
Electrical Engineer
Kabul Afghanistan