I know that this sounds like something that was settled in the dark ages but I have a somewhat different twist on the problem.
Non-residential occupancy. Consider a branch circuit with a string of dedicated receptacles that serve instruments that are unlikely to be moved. All instruments may be used simultaneously but each instrument draws only about 0.5A at 120V, that is, about 60W. For load calculations in the context of NEC 220.14 would it be permissible to calculate the number of allowable receptacles on the branch circuit by using 60W for each receptacle load, rather than the 180W indicated in 220.14(J), since these receptacles are dedicated to known loads and are not general purpose?
On the one hand, logic would tell me yes since I know the loads, on the other hand I can't find anything in the Code that would allow that.
Would appreciate your usual incisive setting me straight.
Heinz R.
Non-residential occupancy. Consider a branch circuit with a string of dedicated receptacles that serve instruments that are unlikely to be moved. All instruments may be used simultaneously but each instrument draws only about 0.5A at 120V, that is, about 60W. For load calculations in the context of NEC 220.14 would it be permissible to calculate the number of allowable receptacles on the branch circuit by using 60W for each receptacle load, rather than the 180W indicated in 220.14(J), since these receptacles are dedicated to known loads and are not general purpose?