The only reason I can see it being unsafe is if there is a remodel job and someones assumes it's dead because it was buried in the ceiling.
Or the home owner goes in attic and grabs it by accident.
I guess I just have different understanding of insulated.![]()
Or the home owner goes in attic and grabs it by accident. I read 300.5 but didnt see where it said it has to be in a box. I know its correct but what part dennis?
300.15 Boxes, Conduit Bodies, or Fittings ? Where Required.
A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed.
Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).
So are you saying it is legal to leave a hot wire in the ceiling with no box?
Well, I see it differently. Art. 300.15 has the method for knob and tube and one for other methods. They certainly are not the same. It appears to me that there are more restrictions on the other wiring methods.
Quite frankly I don't see it as that unsafe either but I do see it as a violation.
Did you think I didn't read it.:grin:Read the section you posted.
Well if you don't see the end of the wire as the termination then I can't make you see it that way. We will just have to see it differently. :grin:I am not convinced a dead ended NM is a termination point.
I just can't imagine the writers of the NEC would say this was allowed.
When I run into a situation like this i like to disconnect from the panel.I was just doing a rewire on a previously added-on (60's or so) laundry room addition. The whole addition was wired off the old porch complete with an open splice where the old porch light was. Obviously done by an DIYer. So I rewired the thing and abandoned the old wiring.
I just hate abandoning wiring in the walls when I can't physically see it along the whole length. I am always afraid it's tied in somewhere else, double feed or something, and the cut off abandoned wires will somehow get hot in the future.
Do you guys think I'm just being a worry wart? I don't know what else to do other than cut 'em off and leave 'em in the wall without tearing the whole thing down to the studs.
A known hot wire obviously belongs in a box. I am talking about wires that you disconnected and rang out. They are dead and abandoned and not part of the premise wiring any more as far as one can tell without actually seeing it. You may think you have found a wire, but you never know, it could be T tapped in the wall and refed off a switched basement light or something crazy like that. The only way to be a 100% sure is to remove it which is not possible.
I like Iwire's plan. I am going to start using heat shrink to encapsulate the end of a piece of abandoned romex.
I don't get the fear of a taped up wire end. :-? I have done this countless times.
i have yet to see somebody show how this is a violation.
you know that doesn't make it code compliant:grin:I don't get the fear of a taped up wire end. :-? I have done this countless times.
I do not tape or connect the wires together, I isolate them from each other with wirenuts and then tape, and then write on the sheath- abandoned cable, do not energize at both ends...