Plug in equipment above suspended ceiling

Status
Not open for further replies.

Sharpie

Senior Member
Location
PA
OK guys, I know this has been discussed before, but I'm still unclear.

Situation: Customer wants me to install a receptacle above suspended ceiling for a cell phone antenna extender/signal amplifier.

I know that I've read that you can't plug equipment in and leave it up in the ceiling.

I also think that I read that the story changes when your plugging in a small transformer (wallwart). That in some instances that's OK.

Can any body clarify the requirements?

Thanks,:confused:
 
The restriction is actally for cords (400.8) so the receptacle is legal.
Art 725 cables only need to address the plenum rating so a transformer with a Art 725 secondary cable could be legal.
 
Well, this space is not used for environmental air. Does that mean it's not an issue and I would not be in violation to proceed?
 
The cord restriction in 400.8 is for ANY suspended or dropped ceiling.
The Art 725 wiring should be acceptable, but not cords.
 
I agree with Gus.

The prohibition is not for "equipment" above a suspended ceiling but rather for flexible cords. (400.8 (2) & (5))

A Class 2 or 3 circuit or equipment can be installed above the suspended ceiling in accordance with Article 725.

Chris
 