Hope all are fine and good. My question is regarding to generator size.
I have designed a project and its final Load is equal to 127 kVA. This is a general load, I mean it is a residential buildings.
I have chosen generator size 135kVA with 3ph, 380 volt, pf=0.8. and we know that this generator can provide only 108 kw real power and 80.27 reactive power.
It is possible to increase or decrease the real and reactive power by setting the governer and field winding of generator but we dont have here any automatic control.
So, my question is this. Since this generator can only provide 108kw and the load is a general residential load with 127kVA pf=0.95 which equals to 120.65kW.
Here now at peak load which equals to 120.65 and generator can only provide maximium 108kW. So, according to me this generator can not provide the peak load and it should be increase one step in size.
Am I right or not please advise me.
Hope all are fine and good. My question is regarding to generator size.
I have designed a project and its final Load is equal to 127 kVA. This is a general load, I mean it is a residential buildings.
I have chosen generator size 135kVA with 3ph, 380 volt, pf=0.8. and we know that this generator can provide only 108 kw real power and 80.27 reactive power.
It is possible to increase or decrease the real and reactive power by setting the governer and field winding of generator but we dont have here any automatic control.
So, my question is this. Since this generator can only provide 108kw and the load is a general residential load with 127kVA pf=0.95 which equals to 120.65kW.
Here now at peak load which equals to 120.65 and generator can only provide maximium 108kW. So, according to me this generator can not provide the peak load and it should be increase one step in size.
Am I right or not please advise me.