I have to determine the approximate cost to make ice for the ice skating event (Disney on Ice) in the local Arena. We have 3 compressors plus a brine pump (the brine pump will run all the time) and the compressors stage until ice is made then one compressor will maintain the ice. The amperage listed is taken off the face of the breaker on the read-out screen. All three compressors will run for 8 hours, 2 will run for another 40 hours then one will run to maintain (we'll use 24 hours which will be multiplied for however many days the event will run.
All pumps for 8 hours - 504 amps x 480v=241,920 x 1.732=
419,005.44 x 8 hrs = 3,352,043.5 /1000 = 3,352kw
2 pumps for 40 hours - 380 amps x 480v= 182,400 x 1.732=
315,916.8 x 40 hrs = 12,636,672 /1000 = 12,637kw
1 pump for 24 hours - 240 amps x 480v= 115,200 x 1.732=
199,526.4 x 24 hrs = 4,788,634 /1000 = 4,789kw
---------
3-day total = 20,778kw
JEA cost per kw x .02214
---------
$460.02
Am I on the right path here not counting demand and kvar?
Thanks,
Jeff