# of Recepticles in a Commercial Tenant Space

Status
Not open for further replies.

tommygary

Member
Location
New York
Can you please tell me if there is a minimum # of recepticles that is required in a commercial tenant space, and where I can find the answer. In regards to a residential location, I believe there is no specific # required. You are able to have an unlimited amount. Please inform. Thank You.
 

jwjrw

Senior Member
There is no required numberin commercial. In residential you have locations where receptacles must be like countertops, within 6ft of a door etc but no restriction on how many. On commercial its figured at 180 va er device.
 

jwjrw

Senior Member
There is no required numberin commercial. In residential you have locations where receptacles must be like countertops, within 6ft of a door etc but no restriction on how many. On commercial its figured at 180 va er device.

With some exceptions that is:D
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
On commercial, if you have HVAC, you must have one per 210.63.
You could, by Code, stop there.
 