jango
I know that the required size of the grounding electrode for a typical 200 Amp service is a #4 solid copper. Now, we are planning on a 400 Amp service and I'm not sure what size PG&E will be running in the 3" PVC service lateral conduit but the length is approx. 300' so I'm assuming a pretty large set of service conductors. Now my question: I see in the NEC book under 250.66 that the required size of the grounding electrode conductor is based on the size of the largest ungrounded service entrance conductor. They already have a #4 solid copper which bonds to the concrete encased steel in the foundation which falls under 250.66(B) so am I fine to assume that based on this, regardless of the new service size being a 400 amp service and regardless of what size the service entrance conductors are, the grounding electrode conductor is code compliant being a size #4 solid copper?