I am installing a new UPS .The UPS in all electronic and is not a transformer type.
Do I have to bond the grounded conductor?
 

tccra

Member
UPS Installation - Bonding/Seperately Derived System

UPS Installation - Bonding/Seperately Derived System

The new UPS is 480V 3 Phase-3 Wire input and output. The UPS output is fed into a 3 wire output distribution panel. Neither the input or output of the UPS requires a grounded conductor (neutral) according to the manufacturer. All UPS downstream loads have step down transformers to reduce the voltage down to 208/120V 3 phase - 4 wire output. No 277V loads are needed in this case. All these downstream transformers are considered seperately derived and have a grounding electrode conductor running to building steel. We do not have a neutral to ground bond (SBJ) connection inside the UPS. Is that okay?
 

RICK NAPIER

Senior Member
Location
New Jersey
There is no grounded conductor to bond in your description. It is not a seperately derived system and does not require a grounded conductor or bonding to one.
 

tccra

Member
UPS Installation - Bonding/Seperately Derived System

UPS Installation - Bonding/Seperately Derived System

Thanks alot for the help....
 