Actually what he used in his calculation is in the OP... "Each hi-bay has six 57W CFLs...".
So we can assume that his calculation is incorrect?
Actually what he used in his calculation is in the OP... "Each hi-bay has six 57W CFLs...".
Perhaps... perhaps not. He does state the lamps are CFL's. The ballasts are integral with the lamp, right? ...thus lamp rating includes ballast. Yet we don't know if the fixture is rated for 57W per lamp or higher (assuming 57W is not higher than the fixture's individual lamp rating).So we can assume that his calculation is incorrect?
He does state the lamps are CFL's. The ballasts are integral with the lamp, right?
When I read 'high bay with 57 watt CFLs' this is what comes to my mind. The ballasts are NIC.
![]()
I did e-mail the manufacturer to see what they had to say, but it looks like I will have to add in a 2-pole contactor for each phase to allow for the load.
When I read 'high bay with 57 watt CFLs' this is what comes to my mind. The ballasts are NIC.
![]()
If non-integrated ballasts are the case, for the lamp pictured, the ballast wattage is about 62W per lamp.That's what first came to my mind, not a screw-in type replacement for an A style, Edison based lamp.
There are two criterion to use lighting fixtures on a greater than 20: a) must be a non-residential installation, and b) fixtures must utilize heavy duty lampholders. [ref: 210.23]
If the cut sheet has no mention of heavy duty lampholders, they likely cannot be used on a greater than 20 amp circuit.
WHAT HAPPENS if we use lighting fixtures on the greater than 20 amps circuits? is it banned?isnt it better since it has a larger ampacity?
Larger ampacity isn't necessarily better (hopefully I don't have to explain that statementWHAT HAPPENS if we use lighting fixtures on the greater than 20 amps circuits? is it banned?isnt it better since it has a larger ampacity?