OK so I am paralleling 5 2500kW Generators and I am installing a NGR to limit my Isc 3p=Isc SLG (heard that was an ANSI standard) and at my genertors I've some 147kA of fault current at each Generator during a fault condition at the Generator itself. I looked at the TCC for a 200kAIC 4000AF circuit breaker and coordinated that with the damage curve of the generator and it appears to be fine. So a generator can take some 150kA of fault current for 1 second or so (reference attached docs). thoughts...