If the fault is in the generator, there won't be much left except melted copper after one second. If the generator is feeding the fault, it might last for one second. You may need to check your generator decrement curves against the circuit breaker trip curves. It is possible that the generator voltage will collapse and the fault current will reduce below the trip value of the generator.
The final fault current from a 2500 kVA generator is usually less than full load current. Initial fault current is determiend by the subtransient reactance which is usuallly about 15-20%, meaning fault currents 5-6 times full load. Final fault current is determined by the system impedance and the generator's synchronous reactance which is in the 200-250% range. Xd=200% means the final fault current will be half rated full load current. How fast the current moves between these two values is shown on generator decrement curves. If the current drops too fast, it can go below the breaker's pick up value and the breaker will stop trying to trip so the fault never clears. The curve shape is a function of the generator design and the type of exciter and voltage regulator used.