We were performing an insulation check on a 3 Phase Delta connected resistive element heater and found that is had an extremely low megger reading to ground of 0Meg. We performed measurement at 500V and 1000V and found 0Megs or a short both times.
Is there something we are missing in regards to measuring a resistive heating circuit that is causing it to look like there is a L-G short somewhere? Or is what we are seeing what we are seeing.
When the L-G reading is checked with a regular meter it reads about 85kohm. So even if power was applied the L-G current would be very minimal is this correct? 277V / 85kohm = 3ma ?
So why would the digital meter read 85kohm while the megger reads 0? Is this just a function of the scale ranges on the two?