Hi everyone. I am new to these forums and this will be my first post. This is my situation. In this hydro vault we have 2 switches installed, 400 amp and 1200 amp 347/600 volt. I am going to use this 1200 amp switch and install a 600 amp disconnect and then splitter in a remote room which is 20m away and size conductors according to 600 amp disconnect.
According to code smaller tap conductors must be 1/3 ampacity of the supply conductors to which they are connected and Tapping conductor maximum length must not exceed 7.5 meter (24.6 ft.)
Im my situation run is more than 7.5 meter. I guess code wont allow me to install 600 amp disconnect in remote space which is 20 meter from hydro vault. So my question is, for a 20 meter run do i have to size my wires according to 1200 amp hydro vault switch and install 1200 amp disconnect in remote room. I hope i explained my situation properly. Thanks guys and i am very happy that i found out about these forums. I will be learning a lot, i am sure.
According to code smaller tap conductors must be 1/3 ampacity of the supply conductors to which they are connected and Tapping conductor maximum length must not exceed 7.5 meter (24.6 ft.)
Im my situation run is more than 7.5 meter. I guess code wont allow me to install 600 amp disconnect in remote space which is 20 meter from hydro vault. So my question is, for a 20 meter run do i have to size my wires according to 1200 amp hydro vault switch and install 1200 amp disconnect in remote room. I hope i explained my situation properly. Thanks guys and i am very happy that i found out about these forums. I will be learning a lot, i am sure.