Gfcb
This thread had been temporarily closed. This action was taken because the nature of the question and the occupation shown in the Original Poster's profile raised a concern that this may have been an attempt by a Do It Yourself person to obtain "how-to" information.
In an exchange of Private Messages, the Original Poster has provided assurances that he is a licensed electrician or electrical contractor or is otherwise authorized to perform electrical installation work, and that the question had to do with a business issue. Therefore, the thread is being returned to the active area. I offer an apology to the OP for the inconvenience and the delay.
I'm assuming you mean a 2-pole ground-fault breaker.
Yes, it will work without a neutral connection for the load. But the pigtail from the breaker will still need to be connected to the neutral bar.
If I remember correctly, the neutral "pigtail" must be connected to a neutral supply for the GFCI to operate properly. There is no requirement for a neutral to be connected to the load side as the breaker "monitors" any wire connected.
(sorry 480, posting at same time)