Not sure if I can do this. I have three receptacles circuits that I would like to share the neutral on. I have to increase the size of the wire for voltage drop.
Circuit A #6 wire .9kw
Circuit B #8 wire .72kw
Circuit C #10 wire .30kw
Can I have the hot wires #6, #8, #10 and then the neutral wire #6 or do I have to increase all of the hot wires to a #6 in order to share the neutral. I have never seen this completed and not sure what the correct answer is. I have not been able to find anything on my searches or in the NEC.
Thanks
Thanks