cohosilver
Member
I have a question on whether or not it is acceptable, NEC approved, to bond the steel water pipe outside an existing masonry building if that is the only common steel pipe that feeds multiple bathrooms within the building? In addition, if the water pipe is on the other side of the existing masonry building from the load center that supplies the building, is it acceptacle to run a GEC sized by 250.66 from the water pipe just outside the entrance of the building to the building steel and then run a GEC sized by 250.66 from the building steel to the ground bar in the panel? In addition, I would run #6 solid cu from two 3/4"x10' ground rods to the ground bar in the panel. There is no exposed rebar or other pipes such as gas. I am trying to ground and bond a number of existing old occupied masonry buildings used for living quarters, offices, kitchens and shower/bathroom areas up to NEC 2008 code.