trainfixer
New member
- Location
- minnesota
I am installing a new sub panel in a new attached garage addition that will be used as a heated shop area. I will be installing the panel recessed into the wall with the front flush with the drywall surface. I will have a clear space 30 inches wide from floor to ceiling for working space. Can I install the following within the working space? One: Light switches to control overhead lights. They will protrude no more than 1 inch into the working space measured from the front of the panel. Two: A baseboard heater that will extend from the left side into the working space 15 inches towards the right and that will protrude no more than 2-1/2 inches into the space as measured from the panel front. Three: A 208 v 30 amp receptacle for a plug connected machine. The receptacle will protrude no more than 1 inch as measured from the panel face and will be to the right of and not directly over the heater.
I would assume this installation to be OK since the working space is includes only parts of the "electrical equipment", nothing protrudes more than 6 inches, and the rest of the space is clear for the proper dimensions. I can see the receptacle might be an issue due to the cord protruding when a plug is installed, but the cord can be removed or restrained.
trainfixer
I would assume this installation to be OK since the working space is includes only parts of the "electrical equipment", nothing protrudes more than 6 inches, and the rest of the space is clear for the proper dimensions. I can see the receptacle might be an issue due to the cord protruding when a plug is installed, but the cord can be removed or restrained.
trainfixer