Yea take a deep breath and get ready for the Superbowl
Why does this application require a SER cable larger than 4/0AL installed to each individual sub panel
Why does this application require a SER cable larger than 4/0AL installed to each individual sub panel
If an aluminum SE cable is used I believe it needs to be 300Kcmil, If an aluminum conductor in a raceway is used it is likely to be allowed to be 4/0
If a copper SE cable is used it should need to be 4/0, if a copper conductor in a raceway 3/0 should be allowed.
I am sure someone will correct me if I am wrong.
Actually you're correct on all counts. IMO if we must have it then the stupid 60 degree SE cable rule should only apply to smaller conductors. Needing #4/0 cu conductors in SE cable but only #3/0 cu in conduit is silly.
Are you guys referring to 230.42 (b) concerning the SEU / SER also the table in 310.15(b)6 refers to the feeder between the main disconnect and the panelboard. Table 310.16 rates #300al for 190amps is this the correct wire based on the 800amp and under rule. I am new to this board and a great example of it's value, I mainly do commercial installation's but try to keep up on the housing side , this would be a time consuming/profit eating mistake in the field. Thanks
No problem, done all the time. But the only reason to use the meter combo would be if the panels were to be located elsewhere violating the closest point of entry rule. Your only problem now is you will need 250mcm Al SER (4) wire to feed the panels (if under 2008) or 3/0 Cu. The panels inside are now sub panels. His heck of a deal may go out the window now that the wire type has changed.
One panel, or whole service? Driven electrode, or interior bonding?Quiz question #1 What size GEC for 400 amp service?
I am still having trouble understanding this, 310.15(6) states for this application the feeder shall be the feeder between the main d/c and the panelboard that supplies all loads for the dwelling unit, where does it say this cannot be a main lug panel or this cannot be applied to interior wiring when your still dealing with a feeder. The picture in the handbook 310.9 shows a typical apartment sub fed panel and says 310.15(6) applies and makes no note of interior or exterior . I am taking most of what is being said here as applying to seu or ser being installed for other purposes inside a dwelling unit
Why does this application require a SER cable larger than 4/0AL installed to each individual sub panel
#4/0 AL SER in this application has an ampacity of only 150 amps.
Besides code rules and perhaps some temperature issues is there any real reason for this?
The code change was to bring SE cable in line with NM cable which already had the 60 degree C ampacity requirement. Other than that I don't recall there being any other substantiation such as the use of SE cable at 75 degrees being unsafe. Someone said well SE and NM look kind of the same so lets make them have the same 60 degree C ampacity. A very poor reason IMO.
I have read that a certain wire company tested 4/0 SE cable in a wall packed with insulation. They loaded the wire to 200amps for several hours and it failed. This gave them ammo to go to the CMP with there test results, that no one can get there hands on, and with some persuasion got the code changed. Could it be just to sell more expensive wire????