I have a situation where I'm upgrading from a 100amp service to a 200amp service for a residential single family dwelling. The existing panel will also be replaced with a 200amp panel and the homeowner wants 200amp rated conductors feeding the new panel. The homeowner is adding central air and a hot tub.
If my understanding of the 2008 Nec is correct, if the SER cable from the 200amp main breaker to the 200amp panel feeds the entire load of the home then Table 310.15(B) can be used and 4/0 al SER cable can be installed.
The issue is that the new location of the meter main with 200amp breaker is on the opposite side of the home from the new 200amp panel. The new A/C unit will be right next to the new 200amp meter main. I plan to install a 200amp meter main with 200amp main breaker with 8-16 circuit breaker spaces. I want to install a breaker at the meter main to feed power to the A/C instead of running all the way to the panel on the other side of the home.
Since the A/C load would not be carried by the SER cable, then the entire load of the home would not be carried by the SER cable, meaning I would now have to use Table 310.16 and the 60 deg. column to size the SER cable.
This makes no sense to me.
I'm reducing the load on the SER cable going to the panel by running the A/C from the meter main instead of the panel, yet I now have to increase the size of the SER cable to the panel?
Is this correct?
Am I missing something here?
Is this correct?