I've never done a 400(320)amp residential service before..Here's what I have in mind for overhead installation. Would appreciate any help hints or corrections....
3" EMT Riser to weatherhead 20' up secured with Kindorff and straps
500mcm copper from meter to lines in
4/0 SEU from meter can to 2 200amp Main Breaker panels
#6 solid from meter can to 2 ground rods 6'apart
#2 stranded from meter can to cold water entrance jumped across water meter
Does this sound right?
Should there be a separate bond between the 2 panels?
Any other considerations?
Thanks!