Pricing a project that specs the following:
- Supply a 2P/30A Breaker
- Run 1200' of 1" Sch40 PVC w/ 3 #10 & 1 #10 G
- Feed 100A Panelboard w/ 2P/30A Main, 2 1P/20A, 6 Spares.
- From this panel feed Irrigation control Module drawing 1A.
Since the panel will initially only draw 1A, VD will not be an issue but at 1200', #10's are not going to get you anywhere near 30A without significant VD.
Here's the question: Is it LEGAL to install this in this manner given that when installation is completed there will only be 1A load on the panel but knowing that it has a 30A potential that could damage a larger load due to VD?
Thanks.