Keep in mind that you are posting in a forum that, for the most part, is geared towards the North American electrical contracting industry. RCD is an IEC term, we use the term "Ground Fault Circuit Interrupter" (GFCI) or Ground Fault Circuit Breaker (GFCB). These systems are different from what people in other countries use RCDs for. Installation codes vary and we only have devices suitable for what our codes require. In some installations the GF device must monitor the Neutral, in other installations it doesn't need to.residual current device
A broken neutral is a fault condition but not one sensed by an rcd/gfci/alci. These devices work by sensing a preset difference in the current passing through the device in both directions. A line-side broken neutral may affect load current, but the difference in current passing through the device in both directions will be unaffected (at least initiallywhy?? if neutral is broken and it causes an imbalance cant we say easily that sum of phasor fields is not zero and it will trip???
What you suggest is a ground fault, not simply a broken (open) neutral. Even so, if the ground fault occurs on the line side of the device, the current difference through the device is not affected.I somewhat disagree Smart. If the neutral is broken, won't the current be searching for some other way back to the source? Possibly through a parallel path provided by a communication ground, or water pipe, etc. Depends on how good this other path is and consequently, how much current flows on these other paths is enough to trip the device.
What you suggest is a ground fault, not simply a broken (open) neutral. Even so, if the ground fault occurs on the line side of the device, the current difference through the device is not affected.
no , just think of the toroidal part, three phase passing through it will induce an unbalanced current and this will trip the device i think, if there will be no trip so why we need to pass the neutral through gfci? so just let 3 phase through the device and it will trip anyhow....
SO it means ?? the device wont trip if there is a fault on the lines and the line side neutral is broken?
I don't think the Neutral to ground bond (which is where the current would spit off) is ever on the line side of a GFI. And I think calling the situation described a ground fault is not accurate, although I do not know where a formal definition of a ground fault exists.
Edit to add: I am talking about at a main disconnect.
On a wye system, an RCD works by comparing current coming in (on the phases) to current going out (on the neutral and on the other phases). If you just measured 3 phases coming in without the neutral, you aren't seeing the whole picture.
Under normal operation of a 3? 4W circuit (service, feeder, or MWBC), the three line and neutral currents sum to zero... but the three line currents by themselves may not sum to zero. This is why the neutral is included in the sensing. It is needed to cancel any normal non-zero sum of the three line currents.I am saying it might trip if the line side neutral is broken. It depends on whether there is enough current taking parallel paths on grounding conductors to make it trip. If there is not an adequate alternate path for the neutral current to take, then it probably won't trip and you may have some very unbalanced voltages.