- Illinois
- retired electrician
In a previous thread there was a discussion of the current load on the circuit when you use a solenoid type tester. The following information is based on using an Ideal Vol-Con #61-076, a Fluke 189 DMM and an Amprobe AMB-6D insulation resistance tester.
First I tried to get the DC resistance using the Fluke and read a value of 23 meg. I then tried the low resistance function of the Amprobe an got a reading of greater than 99.9 ohms with a current of 220 mA. I also tried the Amprobe at 500 volts and got a reading of less than 0.01 meg. I am not sure what else is in the Vol-Con, but it does not appear that I am reading directly across the solenoid coil itself.
I then measured the acutal current draw at 122 volts and at 244 volts. I measured both steady state current and peak current (the resolution of the Fluke for peak current is 2.5?s). At 122 volts the peak was 40.5mA and steady state was 25.8mA. At 244 the peak was 87.8mA and steady state was 55.8mA.