That puts a fly in the ointment. Very unusal from mt experience. All the ones I have seen had a 240/24 control transformer.I guess another concern is that there is the controls use a 120v to 24v transformer.
If you need 120v, you'll need to use a 'real' transformer, not a buck-boost.I guess another concern is that there is the controls use a 120v to 24v transformer.
I guess another concern is that there is the controls use a 120v to 24v transformer.
That puts a fly in the ointment. Very unusal from mt experience. All the ones I have seen had a 240/24 control transformer.
In that case, a buck & boost would not be your answer.
While true, I'm with augie in that my experience has 230/208-rated equipment never having a 120 x 24V control transformer (though it may have a "universal" multi-tap control transformer which just happens to have a 120V tap/option). Besides, wouldn't the nameplate/spec's have to call for 120V also?If you need 120v, you'll need to use a 'real' transformer, not a buck-boost.
No. As with any load, the voltage between the two supply conductors is all that matters.I looked at the control transformer and it is a multi tap. however it has a commom and one lead for each voltage so wouldn't that still be 120v to common.
Sounds good to meWhat i am understanding is, that I wire the buck-boost from 277v primary to 230v or 208v secondary, I will have one leg that will be lets say 230v and a neutral . From there I wire the contactor of the heat pump L1 would be the 230v leg and L2 would be the neutral and make sure the control tarnsformer is wired for 230v. The control transformer has a common and one orange for 230v, so I would wire common to L2 neutral side of contactor and orange to L1 or 230v side of contactor.