PetrosA
Senior Member
- Location
- Lancaster, Pennsylvania
Here's a very basic illustration if it will help. The top panel is your main panel, the bottom is the sub panel. In the main panel, there is one 25A main breaker feeding one 16A RCD and one 16A non RCD. The RCD breaker has four poles, one for each of three phases and a neutral. The regular breaker has three poles for each of the phases. In the sub panel, the top rail is for RCD protected circuits only. The neutral bar on the left comes from the N output of the 16A RCD breaker in the main panel and any neutral from a RCD protected circuit would have to be connected here. The bottom rail is fed from the non-RCD breaker in the main panel and circuits fed from this rail would have to use the neutral bar on the right which is connected directly to the main neutral. If you connected a neutral from a circuit on the bottom rail to the left neutral bus, the RCD would trip.