NEC section 430 and industry standards are different...Been looking into this and can't seem to understand it fully.
The motor calculations part 1 and 2 in the Mike Holt's forum stipulates sizing overload protection at the motor at 125% (per NEC 430.32) and the short-circuit/ground-fault per NEC 430.52 (175%, 250%, etc).
My old "cheat sheets" and what seems to be industry standards for sizing of protection is to match the circuit breaker size and disconnect & fuse sizes the same values at the higher %.
For example, a 30HP (40FLA) motor at 480, 3PH according to my sheet would have a 70A/3P circuit breaker in the panel with a 100A disconnect and 70A fuses located at the motor with #6 wire.
But isn't that a violation of NEC 430.32? Wouldn't I need 50A fuses?
Am I missing something here? My other thought is if the motor has a controller with the proper overload protection but then why have a CB and fused disconnects as well?
Any help would be much appreciated.