W wire monk Member Feb 17, 2010 #1 Could you tell me how far you can run 10 thhn on a 30 amp circuit for a portable trailor?? To be up to code..
Could you tell me how far you can run 10 thhn on a 30 amp circuit for a portable trailor?? To be up to code..
Buck Parrish Senior Member Location NC & IN Feb 17, 2010 #2 It depends on volts and load, underground or in air.
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Feb 17, 2010 #3 wire monk said: Could you tell me how far you can run 10 thhn on a 30 amp circuit for a portable trailor?? To be up to code.. Click to expand... To the moon and back. For your install there is no NEC code requirement for voltage drop.
wire monk said: Could you tell me how far you can run 10 thhn on a 30 amp circuit for a portable trailor?? To be up to code.. Click to expand... To the moon and back. For your install there is no NEC code requirement for voltage drop.
Buck Parrish Senior Member Location NC & IN Feb 17, 2010 #5 wire monk said: 240 volt underground Click to expand... Load ??...........
Buck Parrish Senior Member Location NC & IN Feb 17, 2010 #6 Monk, Try this one, their are seveal on the net. I think this is the best one. http://www.csgnetwork.com/voltagedropcalc.html
Monk, Try this one, their are seveal on the net. I think this is the best one. http://www.csgnetwork.com/voltagedropcalc.html
Buck Parrish Senior Member Location NC & IN Feb 17, 2010 #8 Your welcome, that's pretty substantial drop at 200 ft, hey?
mivey Senior Member Feb 18, 2010 #9 chris kennedy said: To the moon and back. For your install there is no NEC code requirement for voltage drop. Click to expand... To the moon, Alice!
chris kennedy said: To the moon and back. For your install there is no NEC code requirement for voltage drop. Click to expand... To the moon, Alice!