Smoke Detectors mounted to a single gang box
iwiremup
Any code issues about mounting smoke detectors to a single gang plastic box instead of a round box? Just curious about this, I saw it the other day and was curious as to what is preferred. I myself prefer the round box.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
I cannot imagine that being an issue.
A/A Fuel GTX
WI & AZ
No problem.....The mounting plates adapt to any kind of box and the single gang's are a lot cheaper than the 4/0's.
al hildenbrand
Minnesota
Electrical Contractor, Electrical Consultant, Electrical Engineer
Next time you open up a line powered smoke, look at the mounting holes in the mounting plate. The smoke manufacturer will almost certainly have a set of holes that are in between the 3.25" and 4" holes of the round box mount. This set of "in between" holes are spaced for the standard wall case screw mount.
My point: The manufacturer has no preference.
480sparky
Iowegia
.......and the single gang's are a lot cheaper than the 4/0's.
raider1
Logan, Utah
Single gang plastic boxes are all I see for smoke alarms.
Here is what the 2008 NEC says about using them.
314.27 Outlet Boxes.
(E) Utilization Equipment. Boxes used for the support of utilization equipment other than ceiling-suspended (paddle) fans shall meet the requirements of 314.27(A) and (B) for the support of a luminaire that is the same size and weight.
Exception: Utilization equipment weighing not more than 3 kg (6 lb) shall be permitted to be supported on other boxes or plaster rings that are secured to other boxes, provided the equipment or its supporting yoke is secured to the box with no fewer than two No. 6 or larger screws.
Chris
walkerj
Baton Rouge
I have always used a single gang.
The first time I saw a round box for a smoke I couldn't figure out why they wanted a light right inside the bedroom door:roll: