A Anwar Pasha Member Feb 18, 2010 #1 Does code stipulates that a certain percentage of space shall be left empty while passing the cable through he PVC pipes laid under ground?
Does code stipulates that a certain percentage of space shall be left empty while passing the cable through he PVC pipes laid under ground?
TOOL_5150 Senior Member Location bay area, ca Feb 18, 2010 #2 Anwar Pasha said: Does code stipulates that a certain percentage of space shall be left empty while passing the cable through he PVC pipes laid under ground? Click to expand... Yes. ~Matt
Anwar Pasha said: Does code stipulates that a certain percentage of space shall be left empty while passing the cable through he PVC pipes laid under ground? Click to expand... Yes. ~Matt
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 18, 2010 #3 Start with Table 1 in Chapter 9 of the NEC and then read through all of the notes to the tables.