What do you all think the answer to this question is?
copper or aluminum???.......
I agree with mr beck i "B" don't know the light load either.copper or aluminum??sorry just saw copper
60.8??prize no prize??
........ The ampacity of a set of 4 current carrying THHN #4 copper will be 95*80%, or 76 amps, even if the actual total connected load is one amp of lighting.
I agree.Ampacity = 76
I agree with this as well. But it wasn't part of the original question.Allowable continuous load = 60.8
You never, Never, NEVER (sorry, I just love to emphasize things that way) "derate" for continuous loads. When you need to make an adjustment for the fact that a load is continuous, you may wind up with a larger wire. But that is not because the ampacity of the wire has been derated. Rather, it is because the load requirements have increased, and you need a wire with more ampacity, which means a larger wire.Are you derating to 80% because of 4 CCCs, or because of continuous load? Why would not both apply?
.......I agree with this as well. But it wasn't part of the original question.
OK. I looked again. The question asks for ampacity. That is a characteristic of the wire, and has no relationship to the load. Try looking up the definition of "ampacity," and tell me where it says anything about the amount, or type, of load that you intend to supply with the wire. It is all about the wire itself, and the conditions under which it is used. The "conditions" refers to the ambient temperature, the number of current-carrying conductors, the ambient environment (i.e., free air versus in conduit versus underground).Look again.![]()
You never, Never, NEVER (sorry, I just love to emphasize things that way) "derate" for continuous loads. When you need to make an adjustment for the fact that a load is continuous, you may wind up with a larger wire. But that is not because the ampacity of the wire has been derated. Rather, it is because the load requirements have increased, and you need a wire with more ampacity, which means a larger wire.
..........The "conditions" refers to the ambient temperature, the number of current-carrying conductors, the ambient environment (i.e., free air versus in conduit versus underground).
Of course they have meaning. And we are bound to follow the rules they provide us.So all those 80%s and 125%s in the Code don't mean anything? I guess I don't understand.