Josh5879
- Rockland County, NY
Hi everyone first time posting here, I already asked this question somewhere else without success so I hope you guys can help me.
What is the proper way to wire a tubular fluorecent fixture that is mounted directly over an outlet box? I am talking about a fixture that is big enough that it can't be supported just from the outlet box, rather it is secured to the ceiling using other means , for example with anchors.
Can you just wire it directly to the conductors in the outlet box? Now I know that that is exactly the way everybody does it, the books I have show it that way, and someone showed me a Mike Holt book with a picture also showing it that way. However I don't think that meets code. Here is*410.24:
"(A) Independent of the Outlet Box. Electric-discharge luminaires supported independently of the outlet box shall be connected to the branch circuit through metal raceway, nonmetallic raceway, Type MC cable, Type AC cable, Type MI cable, nonmetallic sheathed cable, or by flexible cord . . ."
So we have a rule here requiring any fluorecent fixture that is "supported independently of the outlet box" be connected to the circuit using only certain methods. In the above situation the fixture is certainly supported independently of the box, the box wouldn't even be able to support the fixture, the fixture is way too heavy. Therefore this rule IS applicable in our situation, the rule now requiring us to connect this fixture using only one of the specified methods, individual conductors brought in from an adjacent not being one of them.
I hope no one tries to argue that part (B) of that section does allow direct wiring from the box, a carefull reading will make it clear that is only requiring access to the box not allowing you to wire the fixture from that box.
(here it is 410.24(B) Access to Boxes. Electric-discharge luminaires surface mounted over concealed outlet, pull, or junction boxes and designed not to be supported solely by the outlet box shall be provided with suitable openings in the back of the luminaire to provide access to the wiring in the box.)