2 questions: grounding and feeders
TOOL_5150
bay area, ca
1: Is 250.122 the table I use to size an EGC for a subpanel [feeder]
2: Where is it permitted or not permitted to feed [2] 200A sub panels off of [1] 200A main breaker. Going to run a 4/0 SER from 200A metermain to a j-box, then down to two 200A MCB panels side by side.
~Matt
~Matt
#1. Yes
#2. As long as all the equipment and conductors are rated not less than the OCPD.
side note: the 2 panels inside could be MLO if you wanted.
~Matt
1- yes 250.122 is ok
2 As long your total load calculation is less than 200 amps you will be ok ( use the correct size of wire for the tap)
#1. Yes
Thank you - You know when you think about something so much, you start to question yourself.. thats what happened to me, LOL.
Yeah, MLO makes sence, but I can get some MCB's for a real good price. :)
~Matt
And SER 4/0 aluminum as an interior feeder only has an ampacity of 150. I'd say it needs to be protected that way.
If in raceway or other approved means, then a tap rule might help, and you wouldn't need the help for xhhw anyway. :roll:
In some of the jurisdictions here the 4/0 SER would be limited to the 60? rating of 150 amps.
~Matt
So in answering the original two questions:
1-Yes
2-Not permitted to use #4/0 SER protected at 200 amps.
If this is a meter main than I see no problem with the 4/0 aluminum as long as it feeds the total load of the dwelling. We are assuming dwelling here.
I would run the 4/0 to one panel then jump to the other panel with a 100 or 125 amp feed.
I'm wondering why you need 80 circuits in the first place with only a 200 amp service?
But the OP stated that this 4/0 from the main would be spliced a an exterio j-box to two sets of conductors.
[215(A)(you meant 2, right?)] requires "the total load" to be carried for that section.
The 4/0, even though it goes to 2 panels, does carry the entire load of the dwelling.
The relationship between the requirements of 338.10(B)(4), 215.2, and 310.16(B)(6) has been much discussed in previous threads and enforcement definitely varies between AHJ's.
Although you may not find anything "concrete", a search thru previous threads using "338.10" will provide you with many minutes of interesting reading.:)
Yes, the first one does, agreed. It is the second sets of conductors (that I assume are SER), that will be interior feeders that I claim need to used at 60 degrees C, or 150 amp max (assuming aluminum).
My understanding is that there is an external meter main then 4/0 ser that goes to a JB then taps to both panels. There are not two sets of conductors.IMO.
~Matt
If they are taps they are not properly protected. If they are simple splices, they may or may not be properly protected, depending on interpretation.