Some more thoughts:
The earth can not provide a reliable path for ground fault current.
Considering the resistance of a "made electrode" is to be 25 ohms or less the voltage drop through the ground path would be so great as to limit the fault current an not very likely to trip a breaker instantaneously.
Also, the neutral can only be grounded at on point. Should the neutral be grounded at another point, that is not only at the service entrance but also at the generator that would permit neutral currents to be conducted on the grounding conductor, "objectionable current."
Please remember that the neutral is with almost all certainty on the common residential generator is bonded to the frame of that generator. Should that generator be used to provide power directly to a home it must be understood that the neutral will be bonded both to the ground at the service entrance and as well as bonded to the grounding conductor at the generator. Doing so will turn neutral currents loose on the grounding conductor and anything that the grounding conductor is supposed to be grounding.
So please don?t forget home a residential generator is intended to be use and how the can be applied incorrectly.
Your point of view would be appreciated on this subject also.
How is this any different from being grounded at the service disconnect and at the POCO transfomer? The grounded conductor is tied to a GES at the service disco and to a separate ground rod at the POCO trans. Sub the gen for the POCO. Same thing.Some more thoughts:
A few years ago, I would have agreed with this statement. Now there a lot of the common portable generators have the neutral floated. It is not connected to anything other than the neutral side of the receptacles on the generator. Even within the same brand, some models have the neutral bonded to the frame and others have it floated....
Please remember that the neutral is with almost all certainty on the common residential generator is bonded to the frame of that generator. ...
This is true. This does not change the fact that the two scenarios; Poco/gen are the same regards ground rods in two remote locations. I won't say that the stray voltage does not exist,just that the powers that be have done nothing to eliminate it. Do we go to the Poco trans pole and disconnect the butt grd. If so how many poles do we have to disconnect before this problem no longer exist?But the POCO doesn't have to play be the NECs rules.
Come to think of it have you ever heard of stray currents?
I think the following paper will illustrate what I'm talking about which is excellent:
Dangers of Stray Voltage and Stray Current
http://www.mikeholt.com/documents/strayvoltage/word/DangersofStrayVoltageandCurrent.doc
It is my opinion that a generator with a floated neutral cannot be used to supply premises wiring.