EMT Corrision Resistance

Learn the NEC with Mike Holt now!

EMT Corrision Resistance

  • EMT (without extra protection) is accepted in concrete and in soil

    Votes: 1 4.5%
  • EMT is accepted in concrete above and below grade, but not in soil

    Votes: 3 13.6%
  • EMT is only accepted in concrete above grade

    Votes: 10 45.5%
  • EMT is not accepted in concrete or soil

    Votes: 8 36.4%

  • Total voters
    22
  • Poll closed .
Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In Art 358.10 where it addresses EMT in concrete and in direct contact with the soil, there seems to be some "judgment" involved.
Without additional corrosion protection, how is this addressed in your area ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am not sure how it is addressed here anymore. One rarely sees EMT in the soil or in concrete unless it is an old install. All the emt I have pulled out of the soil had been rusted pretty badly and in some case all the way thru the conduit.

Basically around here it is PVC or rigid, not EMT. Not sure how to vote on the poll since it isn't done.
 

jamesoftn

Senior Member
Location
TN
I was looking at a job and questioned the EC about using EMT in above ground slabs (poured floor mulit-story office) in a building. He produced manufactures information that this was approved in above ground slabs only.
 

Buck Parrish

Senior Member
Location
NC & IN
I was looking at a job and questioned the EC about using EMT in above ground slabs (poured floor mulit-story office) in a building. He produced manufactures information that this was approved in above ground slabs only.

We have done it like this for a local iniversity . It's a 5 story building. We put duct tape around the compression couplings.
Underground rust very quickly in NC. It might be okay in AZ.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
From the UL Guide information for Electrical Metallic Tubing (FJMX).
Galvanized steel electrical metallic tubing installed in concrete on grade or above generally requires no supplementary corrosion protection. Galvanized steel electrical metallic tubing in concrete slab below grade level may require supplementary corrosion protection.
In general, galvanized steel electrical metallic tubing in contact with soil requires supplementary corrosion protection. Where galvanized steel electrical metallic tubing without supplementary corrosion protection extends directly from concrete encasement to soil burial, severe corrosive effects are likely to occur on the metal in contact with the soil.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I just don't see why they don't just disallow emt in the soil. There are enough other methods that are better and cheaper (PVC) then emt.
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I worked 1 govmt job with a large co. We put EMT in poured cinder block walls. I never thought to ask then how the EMT was protected. I have seen a lot of it corroded to pieces in concrete or soil, and seen a little that took it ok. We taped couplings too. I agree that PVC is best for such, or rigid if subject to severe damage somehow.
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
We have done it like this for a local iniversity . It's a 5 story building. We put duct tape around the compression couplings.
Underground rust very quickly in NC. It might be okay in AZ.

It ain't okay here. IMC or RGC wrapped in 20mil tape as benaround mentioned.
 

hurk27

Senior Member
I been on a few demo jobs where the EMT was exposed in the demolation, and for the most part the EMT in concrete that was at or above grade barely had any corrosion, but where the concrete was below grade there wasn't much left of it, also I have notice where EMT was strapped in direct contact with concrete or block it would corrode but if it is spaced away from the block by a ?" it would do just fine, even on a wood surface where dirt can collect would cause it to rust, so we use one hole clamps (mineral-lacs) so there is a space between the building and EMT.
 