EMT Corrision Resistance
Learn the NEC with Mike Holt now!
  • EMT (without extra protection) is accepted in concrete and in soil
    Votes: 1 4.5%
  • EMT is accepted in concrete above and below grade, but not in soil
    Votes: 3 13.6%
  • EMT is only accepted in concrete above grade
    Votes: 10 45.5%
  • EMT is not accepted in concrete or soil
    Votes: 8 36.4%
  • Total voters
    22
  • Poll closed .
augie47
Tennessee
In Art 358.10 where it addresses EMT in concrete and in direct contact with the soil, there seems to be some "judgment" involved.
Without additional corrosion protection, how is this addressed in your area ?
I am not sure how it is addressed here anymore. One rarely sees EMT in the soil or in concrete unless it is an old install. All the emt I have pulled out of the soil had been rusted pretty badly and in some case all the way thru the conduit.
Basically around here it is PVC or rigid, not EMT. Not sure how to vote on the poll since it isn't done.
I was looking at a job and questioned the EC about using EMT in above ground slabs (poured floor mulit-story office) in a building. He produced manufactures information that this was approved in above ground slabs only.
We have done it like this for a local iniversity . It's a 5 story building. We put duct tape around the compression couplings.
Underground rust very quickly in NC. It might be okay in AZ.
From the UL Guide information for Electrical Metallic Tubing (FJMX).
Galvanized steel electrical metallic tubing installed in concrete on grade or above generally requires no supplementary corrosion protection. Galvanized steel electrical metallic tubing in concrete slab below grade level may require supplementary corrosion protection.
In general, galvanized steel electrical metallic tubing in contact with soil requires supplementary corrosion protection. Where galvanized steel electrical metallic tubing without supplementary corrosion protection extends directly from concrete encasement to soil burial, severe corrosive effects are likely to occur on the metal in contact with the soil.
I just don't see why they don't just disallow emt in the soil. There are enough other methods that are better and cheaper (PVC) then emt.
I worked 1 govmt job with a large co. We put EMT in poured cinder block walls. I never thought to ask then how the EMT was protected. I have seen a lot of it corroded to pieces in concrete or soil, and seen a little that took it ok. We taped couplings too. I agree that PVC is best for such, or rigid if subject to severe damage somehow.
It ain't okay here. IMC or RGC wrapped in 20mil tape as benaround mentioned.
I been on a few demo jobs where the EMT was exposed in the demolation, and for the most part the EMT in concrete that was at or above grade barely had any corrosion, but where the concrete was below grade there wasn't much left of it, also I have notice where EMT was strapped in direct contact with concrete or block it would corrode but if it is spaced away from the block by a ?" it would do just fine, even on a wood surface where dirt can collect would cause it to rust, so we use one hole clamps (mineral-lacs) so there is a space between the building and EMT.