Took my county masters exam today. (the nail biting begins)
There were 2 or 3 questions that I was sure I knew, but my answer wasn't one of the choices.
One that I remember fairly well was about a restaurant service using the optional calculation.
200kva gen. lighting and small appliances
175kva other appliances
30kva heat
20kva cooling
Gas stoves and steam tables
I came up with 425 kva. I used Table 220.88(not all electric column) Then took 45% of the amount over 325 which is 45% of 100=45kva
45+262.5=307.5KVA
That wasn't any of the choices. I remember one was 425, and the other choices were low 200's.
I'm pretty sure I'm repeating the details correctly.
Do I do something wrong?