On a residential remodel may a twin breaker be added to an existing 42 circuit panel. I did a load calculation and there is lots of capacity. Is this allowed per 408.54 in the 2008 code?
In the 05 book we used to refer to 408.35 which limited you to a maximum of 42 poles. This was deleted in the 08 book, it now states the number of circuits the panel is listed for. So if your panel was made for 42 circuits you can not add anymore. To use mini breakers, the panel must be listed for mini breakers.
Sound like you need to add a sub-panel to make this job compliant.![]()
If the panelboard is listed to accept tandem breakers, I don't see why it would be a problem.
If this puts you over the maximum number of breakers allowed by the panel listing it could not be used.
The Code pretty much spells it out...In the 05 book we used to refer to 408.35 which limited you to a maximum of 42 poles. This was deleted in the 08 book, it now states the number of circuits the panel is listed for. So if your panel was made for 42 circuits you can not add anymore. To use mini breakers, the panel must be listed for mini breakers.
Sound like you need to add a sub-panel to make this job compliant.![]()
408.54 Maximum Number of Overcurrent Devices. A
panelboard shall be provided with physical means to prevent
the installation of more overcurrent devices than that
number for which the panelboard was designed, rated, and
listed.
For the purposes of this section, a 2-pole circuit breaker
or fusible switch shall be considered two overcurrent devices;
a 3-pole circuit breaker or fusible switch shall be
considered three overcurrent devices.
The Code pretty much spells it out...
If for some reason you can install more overcurrent devices than the panel is designed, rated, and listed for, then the panelboard is non-compliant... not installing the tandem breaker... so even installing a subpanel does not make the panelboard compliant if this be the case.
That's the way I see it in part. The other part is it also prevents one from reusing or reconfiguring any older, non-compliant panelboard (but I doubt that compliance would even be checked in most cases).The way it's worded makes this seem like more of a requirement for panelboard manufacturers than the electrician installing the circuit breakers.
I'm still not clear on why tandem breakers are a problem if the panel is listed for it.
Yes it would.But if a 42-pole panel is listed for tandem breakers, doesn't that technically mean the maximum number of circuits the panel is listed for would be 84?
If the panel was installed prior to 2008 code being adopted and compliant with the maximum of 42 circuits installed everything is okay.Mini breakers would count as 2 poles. If the box is rated for 42 cir that is the same as 42 poles. Being this is an older panel, we know it is not listed for more than 42 circuits.
Which is why I stated a sub-panel would need to be used. Move two circuits from the existing panel into the sub to make room for the sub breaker. That is how a sub would make this install compliant.![]()
Not necessarily. It may be listed at 42 "spaces"., but that does not automatically mean 84 circuits via tandems.Yes it would.
I think we said the same thing just differently. It does not matter what code it is installed under if it is listed at 42 circuits max. I have not seen a residential panel listed for more than 42 circuits yet, does not mean it is not out there.
The OP said a 42 cir panel, if it is listed as a 42 cir panel you can not under any circumstances install more than 42 circuits in it. If it is not listed for mini breakers you can not install mini breakers in it.![]()
But if a 42-pole panel is listed for tandem breakers, doesn't that technically mean the maximum number of circuits the panel is listed for would be 84?
No, absolutely not. In fact, as others have said, it wasn't until 2008 NEC that panelboards were allowed to have more than 42 cir. I have not seen one yet but I hear that Sq. D has made a 60 cir. panel.But if a 42-pole panel is listed for tandem breakers, doesn't that technically mean the maximum number of circuits the panel is listed for would be 84?
Many panels are mark with 20/40 circuits. This means 40 full size breakers or 20 twins. Either way it is 40 circuits max.
That pretty much sums it up. Check the panel label, obey it, simple!
SQ D now has load centers that accept up to 60 circuits. 40/50 and 42/60 in QO and Homeline