No
All receptacles in wet or damp locations must be WR
(b) wet locations.
(1) 15- and 20-ampere receptacles in a wet location. 15- and 20-ampere, 125- and 250-volt receptacles installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. All 15- and 20-ampere, 125- and 250-volt nonlocking receptacles shall be listed weather-resistant type.
they dont make regular WR receptacles yet correct?
Now say you have a screened in porch... Is that a wet location of could you use weatherproof covers and regular receptacles instead of WR and inuse covers?
I think that Jrjrw was also asking if an in use cover must be used on the porch as opposed to a standard weatherproof cover.It is a damp location and covers do not change that one way or the other.
406(B) Wet Locations.
(1) 15- and 20-Ampere Receptacles in a Wet Location. 15- and 20-ampere, 125- and 250-volt receptacles installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. All 15- and 20-ampere, 125- and 250-volt nonlocking receptacles shall be listed weather-resistant type.
they dont make regular WR receptacles yet correct?
Is that a wet location of could you use weatherproof covers and regular receptacles instead of WR and inuse covers?
It is a damp location and covers do not change that one way or the other.
I think that Jrjrw was also asking if an in use cover must be used on the porch as opposed to a standard weatherproof cover.
No
All receptacles in wet or damp locations must be WR
Im not even familiar with the wr gfci and wr reg rec, I just install the regular ones in a in a wr in use cover. Are the wr rec expensive ?The inspectors dont even flag you or that here
Are you 2005 or 2008?
406.8(b)........
So does that mean you can use the locking rec if the wr is not availiable?
Maybe, but I don't read it that way.![]()