tkb Senior Member Location MA Feb 25, 2010 #1 On a Square D Thermal Magnetic breaker, what does the Min/Max slide adjustment do? Is it a time setting or a current setting?
On a Square D Thermal Magnetic breaker, what does the Min/Max slide adjustment do? Is it a time setting or a current setting?
ron Senior Member Location New York, 40.7514,-73.9925 Feb 25, 2010 #3 Almost always it is a current setting for the instantaneous trip portion of its characteristic.
tkb Senior Member Location MA Feb 25, 2010 #4 cold fusion said: which model breaker? Cf Click to expand... q4l.........
C Cold Fusion Senior Member Location way north Feb 25, 2010 #5 tkb said: q4l......... Click to expand... Ron nailed it. SQD docs agree. cf