I understand what 110.14(c) says. It says that if its under a 100 amps , I can use a higher temperature rated conductor(THHN), as long as I size it with the 60c column in table 310.16. For example, I have a 50A range receptacle with 60c terminals. If I use THHN, you go to 310.16 and size that wire according to the 60c column because of the terminals, and its a 6 AWG.
Now my question is, what if that receptacle was located in an ambient temperature 100F? Which correction factor column at the bottom of 310.16 would I use, the 90c because of the THHN or 60c because of the terminals?
Now my question is, what if that receptacle was located in an ambient temperature 100F? Which correction factor column at the bottom of 310.16 would I use, the 90c because of the THHN or 60c because of the terminals?