peter d
- New England
And more money spent on cable
It's very marginal compared to the speed of not having to pull everything through holes. The labor more than makes up for a bit of extra cable.
In some part of New England all wood framed buildings have furring strips
I agree, and I use the same method. Drill straight down into crawl at every box. Put a man in the crawl and a man up top. You can rough in a house in NO TIME... alot quicker than drilling everything and fishing through holes. But 08' code is gonna slow this method down a bit. But we're still on 05'
We aren't allowed to wire a house until the building is completely closed up.
I must confess ignorance on this matter. We are still on the 2005 code and I am only casually aware of the changes in the 2008 code. What changes are you referring to that will slow this down?
Thanks!
334.15 Exposed Work.
(C) In Unfinished Basements and Crawl Spaces. Where cable is run at angles with joists in unfinished basements and crawl spaces, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards. NM cable installed on the wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing or shall be protected in accordance with 300.4. Conduit or tubing shall be provided with a suitable insulating bushing or adapter at the point the cable enters the raceway. The NM cable sheath shall extend through the conduit or tubing and into the outlet or device box not less than 6 mm (? in.). The cable shall be secured within 300 mm (12 in.) of the point where the cable enters the conduit or tubing. Metal conduit, tubing, and metal outlet boxes shall be connected to an equipment grounding conductor.
In the winter time I hate when builders want a rough wire before the windows and doors are in.
In a perfect world the windows and doors are in and the finished exterior is also in place so that coach lamps boxes and such can be installed flush to finished surface.
He is referring to the section that is requiring running boards for wires in the crawl. The other option is drilling the floor joists in the crawl. :roll: The words Crawl Space was added to this article
The GC and me put plastic over the windows. I have my own heat so it was pretty nice in there today!
Oh and this isn't in Holden. It's in Rutland which happens to be far more backwoodsy!![]()
Yeah, but it's only the next town over!![]()