J-R
 - New Jersey
Could someone confirm for me when using HCF MCAP it is allowed  not to bond green equip ground conductor to box for isolated ground recepicles as 250.146d  Thanks for the help
			Correct. You basically treat it like a circuit conductor until it reaches the MBJ point.I believe the equipment ground for an isolated grounding receptacle can pass through boxes and enclosures unbonded all the way back to the panel where the circuit originated.![]()
Then you bond it where this buildings electrodes land.What if the MBJ is in a different building?
If I am installing an isolated ground circuit do I have to ground first to the metal box of the receptacle and then straight back to the panel or from the receptacle straight back to the panel without grounding to the box?
FPN 250.146(D) Correct me if I am wrong but you need a seperate EGC for the box and raceway seperate from the isolated EGC
Go to www.ecmweb.com/mag/electric_basics_isolated_grounding/index.html
Not so sure I agree with all of this information but would like to get some responses back on this subject. Basically I feel if the isolated ground receptacle conductor is not ran back to the main panel/system ground you are wasting your time and dollars installing this equipment. Just use regular receptacles.
Which information are you disagreeing with?
I agree that the IG to be of any use must be run back to the point where the neutral and ground are bonded together.
We did a floor in a commercial bldg. that was powered from 2 200A subpanels.
In certain areas, Isolated Ground receptacles were spec'd, and those had a separate ground conductor that landed at the equipment ground bus at a subpanel.
The alternative would have been an additional run of approx. 200 ft, mostly straight down, to bsmt. and SBJ location.
The engineer signed off on our installation, but as we know some engineers will sign off on a ham sandwich--(not the ones in the forum, of course)
Is the setup as described "of any use" ?